dew point and temperature graph

Everything that didn't fit in any other topic
Post Reply
serenewongsa
WUFI User
WUFI User
Posts: 7
Joined: Fri Jul 27, 2007 4:20 am -1100

dew point and temperature graph

Post by serenewongsa » Thu Sep 13, 2007 9:38 am -1100

I ran WUFI for a wall section of brick, air layer, vapor retarder, gypsum sheathing, batt insulation, and interior sheathing. In the quick graphs, the temperature and dew point lines appear to be overlapping at several positions in the all of the layers. However, if I zoom in very closely, the lines are not exactly touching but are parallel. If the temp and dew point lines don't touch when zoomed all the way in, does that mean condensation did not actually occur?


Thanks.

Manfred Kehrer
WUFI International Support Team
WUFI International Support Team
Posts: 350
Joined: Thu Mar 10, 2005 2:17 am -1100
Location: Northbrook, IL; USA
Contact:

Post by Manfred Kehrer » Thu Sep 13, 2007 7:09 pm -1100

Yes this means that no condensation occurs and the RH is always below 100%. But an RH of about 95% for instance for a longer time can also be a problem for some material (wood, organic material, ...)
Manfred
Wiss, Janney, Elstner Associates, Inc.
Official WUFI® Collaboration Partner for USA/Canada
Enjoy WUFI® :) .... It is easy and complex.

serenewongsa
WUFI User
WUFI User
Posts: 7
Joined: Fri Jul 27, 2007 4:20 am -1100

Post by serenewongsa » Fri Sep 14, 2007 2:22 am -1100

Hi Manfred,

If there's no condensation, how does the water content in the material go up? How can I find out the paramenters of what's bad for materials like the 95% for wood, etc.? And how long does the 95% have to be sustained to be a problem?
Thanks.
Serene

Manfred Kehrer
WUFI International Support Team
WUFI International Support Team
Posts: 350
Joined: Thu Mar 10, 2005 2:17 am -1100
Location: Northbrook, IL; USA
Contact:

Post by Manfred Kehrer » Sun Sep 16, 2007 8:34 pm -1100

serenewongsa wrote:If there's no condensation, how does the water content in the material go up?
Please take a look at the moisture storage function of the materials. There is defined how much water content a material can store depending of the RH of the enviroment. The physical process is called capillary condensation and this means that in very small capillary's condensation can happen below 100 % R.H.
serenewongsa wrote:How can I find out the paramenters of what's bad for materials like the 95% for wood, etc.? And how long does the 95% have to be sustained to be a problem?
At this time there are less exactly defined rules.

The state of the art is
1) the water content of wooden material should be below 20 M.-%, if temperature is over 10°C
2) German standards say that water content at layer´s boundary should be below 0,5 kg/m²
3) RH of indoor surface should stay below 80% because of mould growth

Manfred
Manfred
Wiss, Janney, Elstner Associates, Inc.
Official WUFI® Collaboration Partner for USA/Canada
Enjoy WUFI® :) .... It is easy and complex.

serenewongsa
WUFI User
WUFI User
Posts: 7
Joined: Fri Jul 27, 2007 4:20 am -1100

Post by serenewongsa » Mon Sep 17, 2007 4:23 am -1100

thanks, manfred. I will take a look at the moisture storage function.

yalinu
WUFI User
WUFI User
Posts: 8
Joined: Fri Jul 11, 2008 10:35 am -1100
Location: New York
Contact:

Post by yalinu » Sat Jul 12, 2008 7:17 am -1100

Can similar criteria be applied to concrete?
For example to keep the moisture content below the storage capacity at RH=80%? Also to keep surface RH<80% for extended periods to prevent mold growth?
The storage capacity of the materials in the library is in units of kg/cu.m. The result graphs also show moisture content by %M.
How can I convert the moisture capacity from kg/cu.m to %M?
Is there a difference in assessing allowable moisture in materials using %M versus kg/cu.m?

Thanks,
Yalin

Manfred Kehrer
WUFI International Support Team
WUFI International Support Team
Posts: 350
Joined: Thu Mar 10, 2005 2:17 am -1100
Location: Northbrook, IL; USA
Contact:

Post by Manfred Kehrer » Sun Jul 13, 2008 7:46 pm -1100

yalinu wrote:Can similar criteria be applied to concrete?
For example to keep the moisture content below the storage capacity at RH=80%? Also to keep surface RH<80% for extended periods to prevent mold growth?
Yalin
Yes, but the growth of mould does also depend on the suface type (Aga-Aga, organic, or mineral)
yalinu wrote: The storage capacity of the materials in the library is in units of kg/cu.m. The result graphs also show moisture content by %M.
How can I convert the moisture capacity from kg/cu.m to %M?
Is there a difference in assessing allowable moisture in materials using %M versus kg/cu.m?

Thanks,
Yalin
to derive water content [mass %] percent, divide the water content [kg/m³] by the bulk density [kg/m³].
Manfred
Wiss, Janney, Elstner Associates, Inc.
Official WUFI® Collaboration Partner for USA/Canada
Enjoy WUFI® :) .... It is easy and complex.

yalinu
WUFI User
WUFI User
Posts: 8
Joined: Fri Jul 11, 2008 10:35 am -1100
Location: New York
Contact:

Post by yalinu » Wed Jul 23, 2008 3:18 pm -1100

Thanks Manfred. Appreciate the prompt response.
Manfred Kehrer wrote: Yes, but the growth of mould does also depend on the suface type (Aga-Aga, organic, or mineral)
I understand that the material is a factor. But if the organic matter is available such as dust, dirt, etc., and the moisture level and temperature is right, growth may happen even on concrete. Is this not right?
It's common in damp basement walls with inadequate damproofing.

Best regards,
Yalin

Manfred Kehrer
WUFI International Support Team
WUFI International Support Team
Posts: 350
Joined: Thu Mar 10, 2005 2:17 am -1100
Location: Northbrook, IL; USA
Contact:

Post by Manfred Kehrer » Wed Jul 23, 2008 7:09 pm -1100

Yes, you are right!
Manfred
Wiss, Janney, Elstner Associates, Inc.
Official WUFI® Collaboration Partner for USA/Canada
Enjoy WUFI® :) .... It is easy and complex.

StrawConstruction
WUFI User
WUFI User
Posts: 7
Joined: Tue Apr 02, 2019 9:36 am -1100

Re: dew point and temperature graph

Post by StrawConstruction » Mon May 13, 2019 8:27 am -1100

Hello, I am interested in the same topic.
I am analyzing a wall construction with WUFI 2D. Is it possible to display the dew point and temperature graph with it? If yes, how?
Thank you in advance.
G.

Christian Bludau
WUFI SupportTeam IBP
WUFI SupportTeam IBP
Posts: 833
Joined: Tue Jul 04, 2006 10:08 pm -1100
Location: IBP Holzkirchen, the home of WUFI
Contact:

Re: dew point and temperature graph

Post by Christian Bludau » Mon May 13, 2019 10:38 pm -1100

No, thats not directly possible in WUFI Graph.
But you could export temperature and RH as ascii and the calculate the dew point.
Christian

Post Reply