Search found 4 matches
- Wed Oct 28, 2020 5:49 am -1100
- Forum: WUFI Pro
- Topic: Relative Humidity in Cavity behind Curtain Wall
- Replies: 1
- Views: 4158
Re: Relative Humidity in Cavity behind Curtain Wall
To add to this question, removing the unvented cavity between the insulation and the glazing unit delivers much more stable results. Ie equilibrium is acheived within two years and the annual cycle of total water is regularly repeated. Therefore, this raises the question of whether the unvented cavi...
- Wed Oct 28, 2020 12:10 am -1100
- Forum: WUFI Pro
- Topic: Relative Humidity in Cavity behind Curtain Wall
- Replies: 1
- Views: 4158
Relative Humidity in Cavity behind Curtain Wall
Hi, I'm looking at moisture accumulation in a wall constructed behind a curtain wall glazed panel. The wall assembly built in WUFI (from inside to out) is: 26mm plasteboard and plaster skim 0.5mm foil faced vapour control layer 150mm mineral wool in metal stud layer. 120mm unventilated cavity (witho...
- Sun Feb 16, 2020 11:15 pm -1100
- Forum: WUFI Pro
- Topic: Assessing a unitised facade
- Replies: 2
- Views: 3834
Re: Assessing a unitised facade
Hi Christian,
This is fantasitically useful. I will implement the measures you suggest and see what happens. I was placing the air leakage into the cavity on the warm side of the sealed unitised facade panel rather than into the panel itself.
Regards
Nick
This is fantasitically useful. I will implement the measures you suggest and see what happens. I was placing the air leakage into the cavity on the warm side of the sealed unitised facade panel rather than into the panel itself.
Regards
Nick
- Sun Feb 16, 2020 12:50 am -1100
- Forum: WUFI Pro
- Topic: Assessing a unitised facade
- Replies: 2
- Views: 3834
Assessing a unitised facade
Hi, I'm modelling a unitised facade. I'm aware that with non porous materials this doesn't fit what WUFI was originally designed for. The external wall assembly (from inside to out) is: Plasterboard vapour control layer Air cavity (with SFS / metsec stud) (no additional moisture storage capability) ...