Simulating attic ventilation

Everything that didn't fit in any other topic
Post Reply
MWE_MOE
WUFI User
WUFI User
Posts: 1
Joined: Sat May 04, 2019 1:45 am -1100

Simulating attic ventilation

Post by MWE_MOE »

I am trying to simulate attic ventilation i af pitched roof.

I have seen examples where the airspace between the truss and insulation has been simulated using 30 mm standard airlayer, 130 mm airlayer without additional moisture with 30 ACH, 30 mm standard airlayer.

Is this the correct way to simulate an atticspace?
Christian Bludau
WUFI SupportTeam IBP
WUFI SupportTeam IBP
Posts: 1161
Joined: Tue Jul 04, 2006 10:08 pm -1100
Location: IBP Holzkirchen, the home of WUFI
Contact:

Re: Simulating attic ventilation

Post by Christian Bludau »

Hi MWE_MOE,
in my eyes, an attic space can not be realistically represented by an air layer. Please keep in mind, that the bigger the airspace is, the more convection will occur. And that can not be expressed by using a source.
It would be better to handle the attic space as a separate room with its own climate, so as a boundary condition in WUFI Pro and not as a layer.

In WUFI the air layers contain effective values for the permeability and the thermal conductivity which include the convection and radiation in the layer. So they always have to be used in thickness given in the database. It is not possible to add air layers with same or different thickness to get a higher thickness. So the example you mention is wrong, if done with WUFI.
Please see also the material information text of the air layers.

Christian
Post Reply