Hi,
is it a way to determine U-value calculation in WUFI 2D using the heat flux profiles? if not, how to determine?
would it be the results accurate and feasible to be considered for a project?
Thanks in advance for the response
U-value calculation for walls using WUFI 2D
-
Alberto Morales
- WUFI User

- Posts: 98
- Joined: Tue Mar 29, 2022 10:57 pm -1100
-
Christian Bludau
- WUFI SupportTeam IBP

- Posts: 1313
- Joined: Tue Jul 04, 2006 10:08 pm -1100
- Location: IBP Holzkirchen, the home of WUFI
- Contact:
Re: U-value calculation for walls using WUFI 2D
The U-value is a steady-state parameter. Therefore, to determine it from WUFI 2D, you should define constant indoor and outdoor boundary conditions and run the calculation until the temperature field and heat flows have reached a steady state.
Once steady-state conditions are reached, the U-value can be derived from the calculated heat flow:
\(U = \frac{q}{T_i - T_e}\)
where \(q\) is the heat flux through the construction in W/m² and \(T_i - T_e\) is the temperature difference between inside and outside.
For a 2D detail, you would integrate the heat flux over the relevant boundary to obtain the total heat flow \(\Phi\) per metre of the detail. For a homogeneous wall section of width \(L\), for example:
\(U = \frac{\Phi}{L \cdot (T_i - T_e)}\)
If the model contains a thermal bridge, the resulting heat flow also includes the additional 2D heat flow caused by the thermal bridge. In this case, it is generally more appropriate to evaluate the linear thermal transmittance (ψ-value) rather than assigning a single U-value to the entire 2D detail.
In practice, however, it is probably easier and more straightforward to determine the U-value and, if relevant, the ψ-value using a dedicated thermal-bridge calculation program, as these programs are specifically designed for steady-state heat-flow calculations.
Christian
Once steady-state conditions are reached, the U-value can be derived from the calculated heat flow:
\(U = \frac{q}{T_i - T_e}\)
where \(q\) is the heat flux through the construction in W/m² and \(T_i - T_e\) is the temperature difference between inside and outside.
For a 2D detail, you would integrate the heat flux over the relevant boundary to obtain the total heat flow \(\Phi\) per metre of the detail. For a homogeneous wall section of width \(L\), for example:
\(U = \frac{\Phi}{L \cdot (T_i - T_e)}\)
If the model contains a thermal bridge, the resulting heat flow also includes the additional 2D heat flow caused by the thermal bridge. In this case, it is generally more appropriate to evaluate the linear thermal transmittance (ψ-value) rather than assigning a single U-value to the entire 2D detail.
In practice, however, it is probably easier and more straightforward to determine the U-value and, if relevant, the ψ-value using a dedicated thermal-bridge calculation program, as these programs are specifically designed for steady-state heat-flow calculations.
Christian
-
Alberto Morales
- WUFI User

- Posts: 98
- Joined: Tue Mar 29, 2022 10:57 pm -1100
Re: U-value calculation for walls using WUFI 2D
Thanks for the reply.
The idea is to analyze the effect of the external climate and moisture in materials in the U-value as you know U value is not constant along the year. There are not static conditions inside and outside of the assembly as it is defined in other software like THERM, FLIXO, etc.
so once explained my idea, would it be the procedure the same to analyze the U value?
The idea is to analyze the effect of the external climate and moisture in materials in the U-value as you know U value is not constant along the year. There are not static conditions inside and outside of the assembly as it is defined in other software like THERM, FLIXO, etc.
so once explained my idea, would it be the procedure the same to analyze the U value?
x
Re: U-value calculation for walls using WUFI 2D
Hi Alberto,
I see two options:
(1) If you are interested in the effect which a specific moisture content which exists at a specific point in time has on the U-value, you could use that moisture distribution as the initial moisture distribution of a separate WUFI calculation, switch off moisture transport (retaining only heat transport) so that the moisture distribution does not change, apply constant boundary conditions, run the thermal-only calculation until steady-state conditions have been reached and analyze the resulting heat flow as explained by Christian.
(2) If you are interested in the "effective" U-value representative for a year or for some season, taking into account all the changing moisture contents which occur during that period, you could simply do the same analysis, based on the total amount of heat which has passed through the component and the mean values of the exterior and interior ambient temperatures.
The background here is that while the U-value is usually defined in terms of steady-state conditions, it also describes in good approximation the long-term total heat flux as dependent on the mean ambient air temperatures. You can not use the U-value to predict the short-term (say hourly) heat flux, because the U-value does not take the heat capacity (and thus the thermal inertia) of the component into account. For example, when the temperature rises, the heat stored in the component is missing from the analysed heat flow and is thus not taken into account by a U-value analysis. But when the temperature drops, the stored heat is added to the analysed heat flow, which is therefore stronger than it should be in a steady situation, and this 'error' tends to compensate the previous 'error'. Since the natural temperature fluctuations are not strictly periodic, this compensation will not be perfect after one (daily) period, but the longer the analysed period of time is, the more negligible is the remaining error in comparison to the total amount of heat that has passed through the component.
This is the reason why the U-value is a useful indicator for the long-term heat loss, even though in reality the component is never really exposed to steady-state conditions.
Regards,
Thomas
I see two options:
(1) If you are interested in the effect which a specific moisture content which exists at a specific point in time has on the U-value, you could use that moisture distribution as the initial moisture distribution of a separate WUFI calculation, switch off moisture transport (retaining only heat transport) so that the moisture distribution does not change, apply constant boundary conditions, run the thermal-only calculation until steady-state conditions have been reached and analyze the resulting heat flow as explained by Christian.
(2) If you are interested in the "effective" U-value representative for a year or for some season, taking into account all the changing moisture contents which occur during that period, you could simply do the same analysis, based on the total amount of heat which has passed through the component and the mean values of the exterior and interior ambient temperatures.
The background here is that while the U-value is usually defined in terms of steady-state conditions, it also describes in good approximation the long-term total heat flux as dependent on the mean ambient air temperatures. You can not use the U-value to predict the short-term (say hourly) heat flux, because the U-value does not take the heat capacity (and thus the thermal inertia) of the component into account. For example, when the temperature rises, the heat stored in the component is missing from the analysed heat flow and is thus not taken into account by a U-value analysis. But when the temperature drops, the stored heat is added to the analysed heat flow, which is therefore stronger than it should be in a steady situation, and this 'error' tends to compensate the previous 'error'. Since the natural temperature fluctuations are not strictly periodic, this compensation will not be perfect after one (daily) period, but the longer the analysed period of time is, the more negligible is the remaining error in comparison to the total amount of heat that has passed through the component.
This is the reason why the U-value is a useful indicator for the long-term heat loss, even though in reality the component is never really exposed to steady-state conditions.
Regards,
Thomas