Dear all,
I'm trying to run a pressurization test on Wufi Plus 3 but every time i start it, i have always the same error: case 2/ building: error in zone air flow model.
What could the cause be?
Best,
Valeria
Pressurization test- Error in Zone Air Flow Model
Re: Pressurization test- Error in Zone Air Flow Model
Hello Valeria,
Are you able to run the simulation? All inputs have to be done.
If the message with the pressurization test doesn't jump to the point were the error occur, it can have several reasons.
- Check the Floor heights above ground for the zones and for the components. If the value isn't caluculated from visualized geometry, set it user defined.
- Check in component->Surface->Air flow-> Data if you have, flow path parameters, might calculated according to air change rate setting (the grey). or if you do individual settings, check if you have at least two flow paths.
if it still doesn't work. you can send me the model via a private message.
best,
Matthias