dew point and temperature graph
I ran WUFI for a wall section of brick, air layer, vapor retarder, gypsum sheathing, batt insulation, and interior sheathing. In the quick graphs, the temperature and dew point lines appear to be overlapping at several positions in the all of the layers. However, if I zoom in very closely, the lines are not exactly touching but are parallel. If the temp and dew point lines don't touch when zoomed all the way in, does that mean condensation did not actually occur?
Thanks.
Thanks.
Yes this means that no condensation occurs and the RH is always below 100%. But an RH of about 95% for instance for a longer time can also be a problem for some material (wood, organic material, ...)
Enjoy WUFI®
.... It is easy and complex.
Enjoy WUFI®
Please take a look at the moisture storage function of the materials. There is defined how much water content a material can store depending of the RH of the enviroment. The physical process is called capillary condensation and this means that in very small capillary's condensation can happen below 100 % R.H.serenewongsa wrote:If there's no condensation, how does the water content in the material go up?
At this time there are less exactly defined rules.serenewongsa wrote:How can I find out the paramenters of what's bad for materials like the 95% for wood, etc.? And how long does the 95% have to be sustained to be a problem?
The state of the art is
1) the water content of wooden material should be below 20 M.-%, if temperature is over 10°C
2) German standards say that water content at layer´s boundary should be below 0,5 kg/m²
3) RH of indoor surface should stay below 80% because of mould growth
Enjoy WUFI®
Enjoy WUFI®
Can similar criteria be applied to concrete?
For example to keep the moisture content below the storage capacity at RH=80%? Also to keep surface RH<80% for extended periods to prevent mold growth?
The storage capacity of the materials in the library is in units of kg/cu.m. The result graphs also show moisture content by %M.
How can I convert the moisture capacity from kg/cu.m to %M?
Is there a difference in assessing allowable moisture in materials using %M versus kg/cu.m?
Thanks,
Yalin
Thanks,
Yalin
Yes, but the growth of mould does also depend on the suface type (Aga-Aga, organic, or mineral)yalinu wrote:Can similar criteria be applied to concrete?
Yalin
to derive water content [mass %] percent, divide the water content [kg/m³] by the bulk density [kg/m³].yalinu wrote: The storage capacity of the materials in the library is in units of kg/cu.m. The result graphs also show moisture content by %M.
Thanks,
Yalin
Enjoy WUFI®
Enjoy WUFI®
Thanks Manfred. Appreciate the prompt response.
It's common in damp basement walls with inadequate damproofing.
Yalin
I understand that the material is a factor. But if the organic matter is available such as dust, dirt, etc., and the moisture level and temperature is right, growth may happen even on concrete. Is this not right?Manfred Kehrer wrote: Yes, but the growth of mould does also depend on the suface type (Aga-Aga, organic, or mineral)
Yalin
Re: dew point and temperature graph
Hello, I am interested in the same topic.
I am analyzing a wall construction with WUFI 2D. Is it possible to display the dew point and temperature graph with it? If yes, how?
Thank you in advance.
G.
G.
No, thats not directly possible in WUFI Graph.
But you could export temperature and RH as ascii and the calculate the dew point.
