Modelling a wall separating a conditioned space from a unconditioned garage

Posted: Mon Aug 16, 2021 11:14 pm -1100
by Rob Petruzzi
Hi,
I'm new to WUFI and I'm trying to model an internal thermal envelope wall separating the conditioned part of a residential house from the unconditioned garage.
In terms of outdoor climate (i.e. the 'climate' of the garage) should I create/modify the weather file to account for the fact that the wall will not be exposed to any rain, wind, direct sun, etc. or is there a simplier way to define this boundary condition?

Thank you in advance.

Rob

Re: Modelling a wall separating a conditioned space from a unconditioned garage

Posted: Tue Aug 17, 2021 12:26 am -1100
by Christian Bludau
Dear Rob,
there are different methods for that:
  • you could assume, that the temperature and relative humidity is the same like outdoor. In this case in the outdoor transfer coefficients set the adhering fraction of rain to zero or no rain and set short wave absorption as well as the long wave emission to zero
  • you could create an user-defined sine curve or also over the year constant with the values you assume in the garage
  • You can create your own climate file using "CreateClimateFile.xlsm" in the WUFI tool folder if you have values for your garage (for that you need at least values for T and RH)

Re: Modelling a wall separating a conditioned space from a unconditioned garage

Posted: Tue Aug 17, 2021 11:49 am -1100
by Rob Petruzzi
Thank you very much for your prompt reply Christian. Much appreciated!