Double vapour barriers indoors
Posted: Wed Mar 08, 2023 4:30 am -1100
Hi,
I've simulated a 1D-construction in WUFI 2D. I don't fully understand my results. I would be pleased for any thoughts! Thank you!
The construction is a wall between a ventilation shaft and a SPA area.
Construction:
Shaft side
1. Plywood 15 mm
2. Alutrix 1mm (SD >1500)
3. Aquaboard 12,5mm (I'm using the standard gypsum board in WUFI. See attached file: GypsumBoard_Data)
4. Vapour barrier 1mm (SD 50)
5. Concrete plaster 3 mm
SPA side
Climate conditions (constant):
Shaft:
Air temperatur: 23 C
Relative humidity: 50% (base on climate file: varying between 45%-55%)
SPA:
Air temperatur: 32 C
Relative humidity: 50%
Result
I'm checking the part of the aquaboard which is closest to the shaft side. Just "inside" the Alutrix barrier. As can be seen on the attached figure "Location for moisture check in Aquaboard".
The result over a 10 year period is displayed in the attached file: Aquaboard_mot torr-sida (it is in Swedish, but I guess it's understandable).
What I see, is that the moisture is slowly accumulating over time until a level of 5 kg/m3 moisture content (or 60% relative humidity).
My question is:
Why do the moisture stop buffering at that level? There should be about 15 kg/m3 moisture available? (which is the levle in the SPA air, and in the concrete plaster) I've tried replacing the SD=50 to SD=20. I've tried replacing the aquaboard/gypsum board to plywood. The result still becomes the same.
Best,
Alice
I've simulated a 1D-construction in WUFI 2D. I don't fully understand my results. I would be pleased for any thoughts! Thank you!
The construction is a wall between a ventilation shaft and a SPA area.
Construction:
Shaft side
1. Plywood 15 mm
2. Alutrix 1mm (SD >1500)
3. Aquaboard 12,5mm (I'm using the standard gypsum board in WUFI. See attached file: GypsumBoard_Data)
4. Vapour barrier 1mm (SD 50)
5. Concrete plaster 3 mm
SPA side
Climate conditions (constant):
Shaft:
Air temperatur: 23 C
Relative humidity: 50% (base on climate file: varying between 45%-55%)
SPA:
Air temperatur: 32 C
Relative humidity: 50%
Result
I'm checking the part of the aquaboard which is closest to the shaft side. Just "inside" the Alutrix barrier. As can be seen on the attached figure "Location for moisture check in Aquaboard".
The result over a 10 year period is displayed in the attached file: Aquaboard_mot torr-sida (it is in Swedish, but I guess it's understandable).
What I see, is that the moisture is slowly accumulating over time until a level of 5 kg/m3 moisture content (or 60% relative humidity).
My question is:
Why do the moisture stop buffering at that level? There should be about 15 kg/m3 moisture available? (which is the levle in the SPA air, and in the concrete plaster) I've tried replacing the SD=50 to SD=20. I've tried replacing the aquaboard/gypsum board to plywood. The result still becomes the same.
Best,
Alice