Message before simulating + diffence in tendency

Posted: Thu Jul 23, 2026 1:23 am -1100
by Alberto Morales
Hi,

I got a message about parameters that I have defined previously but, the software detects as an error...so my concern is if the results will not be accurate...
error.PNG
error.PNG (151.99 KiB) Viewed 5521 times
h,hj.PNG
h,hj.PNG (42.79 KiB) Viewed 5521 times
in terms of ach, what is the range of ach for a pitched roof with strong, normal and low ventilation?

Re: Message before simulating + diffence in tendency

Posted: Thu Jul 23, 2026 4:14 am -1100
by Christian Bludau
Hi Alberto,
the warning indicates that heat transfer coefficients have been defined for the pitched roof model, but the corresponding reduction factors have not been specified. These reduction factors can be selected from the "Reduction Factors" drop-down menu.

This warning does not necessarily mean that your simulation results are inaccurate, but you should review and complete these settings to ensure the model is configured as intended.

For more information, please refer to the "Pitched Roof" guideline, which explains the purpose and correct use of the reduction factors in detail.
https://wufi.de/en/service/downloads/#pitched_roofs
Christian

Re: Message before simulating + diffence in tendency

Posted: Thu Jul 23, 2026 9:15 pm -1100
by Alberto Morales
Hi,

Thanks for you reply. i have followed that guidance.

Could you add a screenshot where to find that ""Reduction Factors" drop-down menu" as I select User-defined?
Capture.PNG
Capture.PNG (50.25 KiB) Viewed 5502 times
Regards

Re: Message before simulating + diffence in tendency

Posted: Wed Jul 29, 2026 8:58 pm -1100
by Christian Bludau
Hi,
the warning simply indicates that the settings do not follow the recommended configuration described in the guideline. If you have a specific reason for using different reduction factors, the warning can generally be ignored.

The recommended settings for the reduction factors are illustrated in the Pitched Roof guideline on page 19:
Pitched Roof Settings
Pitched Roof Settings
pitched roof.png (96.32 KiB) Viewed 5379 times
Christian

Re: Message before simulating + diffence in tendency

Posted: Wed Jul 29, 2026 9:00 pm -1100
by Christian Bludau
The settings for PV-modules would be on page 21:
pv_modules.png
pv_modules.png (202.13 KiB) Viewed 5379 times

Re: Message before simulating + diffence in tendency

Posted: Thu Jul 30, 2026 9:49 am -1100
by Alberto Morales
thanks but the error is showed when I define the reduction factor for the coldest and warmest position of a ventilaed roo so, I add user defined reduction factors

Re: Message before simulating + diffence in tendency

Posted: Fri Jul 31, 2026 1:30 am -1100
by Christian Bludau
Hi Alberto,
it is a warning, not an error.
If you have a specific reason for setting these reduction factors, the warning can generally be ignored.
Only the center position is included in the surface calculation, which is why this warning is displayed. If you are using different positions, you can safely ignore the warning.
Christian

Re: Message before simulating + diffence in tendency

Posted: Fri Jul 31, 2026 9:50 pm -1100
by Alberto Morales
thanks. i appreciate your help