what sort of Heat Transfer Coefficient would you assign to a surface that is seeing external climate without the solar gains as in the case of a concrete slab on the underside of pilotis?
I am including a picture to better understand the scenario
Cheers
Chris
Pilotis-Heat Transfer Coefficient
-
- WUFI User
- Posts: 8
- Joined: Tue Oct 09, 2018 9:28 pm -1100
- Contact:
Pilotis-Heat Transfer Coefficient
- Attachments
-
- k2.jpg (29.01 KiB) Viewed 6556 times
Pharmacie rentable www.viagrasansordonnancefr.com les soins aux patients
-
- WUFI SupportTeam IBP
- Posts: 1157
- Joined: Tue Jul 04, 2006 10:08 pm -1100
- Location: IBP Holzkirchen, the home of WUFI
- Contact:
Re: Pilotis-Heat Transfer Coefficient
Hi Chris,
I would assign indoor, because the radiation part is set that way that it includes the corresponding walls.
In the 8 W/m²K half is convective and half is radiative part.
Best regards,
Christian
I would assign indoor, because the radiation part is set that way that it includes the corresponding walls.
In the 8 W/m²K half is convective and half is radiative part.