ACH for a ventilated cavity

Post by eordner »

I'm modeling a wall system with a terra cotta rainscreen and would like to model the cavity behind the rainscreen with an Air Change Source. What is the appropriate way to approximate a ventilated cavity? (i.e.- accurate values for ACH) Also, does WUFI read excel files for the air change source?
Manfred Kehrer
WUFI International Support Team
WUFI International Support Team
Posts: 351
Joined: Thu Mar 10, 2005 2:17 am -1100
Location: Northbrook, IL; USA
Contact:

Post by Manfred Kehrer »

There is an example file (AirChangeRate.txt) in the project folder and also a Example Project (Example_USA_Leakage_Vent.w4p) showing you how to do it.
Manfred
Wiss, Janney, Elstner Associates, Inc.
Official WUFI® Collaboration Partner for USA/Canada
Enjoy WUFI® :) .... It is easy and complex.
Talev
WUFI User
WUFI User
Posts: 4
Joined: Tue Dec 06, 2011 8:22 am -1100
Location: Oslo, Norway

AirChangeRate

Post by Talev »

Dear WUFI users,

I am wondering if there any who can tell me where can I find example file (AirChangeRate.txt) in the project folder and also a Example Project (Example_USA_Leakage_Vent.w4p)? I get a signal that it shows how I can do ACH txt file.

I look forward to hering from you!

Regards,

Talev

I hvae found solutions
Christian Bludau
WUFI SupportTeam IBP
WUFI SupportTeam IBP
Posts: 1160
Joined: Tue Jul 04, 2006 10:08 pm -1100
Location: IBP Holzkirchen, the home of WUFI
Contact:

Post by Christian Bludau »

Hi Talev,

you can find the files in your program folder under \IBP-Software\WUFI5\Projects\.

The AirChangeRate.txt is a simple ASCII File with two columns, first one is time [h] and second one airchange in [1/h].
For specific information see the help file in the sources section.

Best regards,
Christian