Critical RH limit for woodfibre IWI at masonry interface

Post by Browne Dan »

Dear Team,

I am wondering what critical limit IBP use for RH at the IWI/masonry interface for a woodfibre based insulation like Steico, Pavatex, Gutex, Homotherm etc. The (presumed) absence of oxygen should mean that the limit is higher than 80%RH, but do you have a safe limit to work to when assessing the results? Any reference-able material would be appreciated.

I am using the RH assessment in addition to assessing the water content by mass percent of the 5mm woodfibre interface layer for critical levels stated in your training literature of >18-20%

Many thanks in advance for any information
Daniel
WUFI SupportTeam IBP
WUFI SupportTeam IBP
Posts: 134
Joined: Tue Jul 19, 2005 2:50 am -1100
Location: Fraunhofer IBP, Holzkirchen
Contact:

RH limit beneath interior insulation

Post by Daniel »

In Germany there are different limits in discussion. The WTA guideline for interior insulations recommends to limt the RH to 95 %.

To avoid mould growth for sure a complete adheseion of the insulation to the substrate is required.

Accoding do Viitanen at 95 % RH and below 10 °C no wood ;-) decay can occur.

best regards
Daniel
Dr.-Ing. Daniel Zirkelbach, Deputy Head of Department Hygrothermics, IBP Holzkirchen
Browne Dan
WUFI User
WUFI User
Posts: 20
Joined: Mon May 25, 2009 1:12 am -1100
Location: London, England

Post by Browne Dan »

Many thanks