explicit radiation balance

Everything that didn't fit in any other topic
Post Reply
Peterbilt
WUFI User
WUFI User
Posts: 7
Joined: Tue Oct 23, 2012 1:58 am -1100

explicit radiation balance

Post by Peterbilt »

I just did a series of WUFI PRO (1-D) runs for a cathedral roof for Madison Wisconsin USA).

The only way I could get the runs to not have more than 1k convergence failures was to unselect "explicit radiation balance" under Surface Transfer Coefficients, even though when I clicked on "run" a dialog "Explicit radiation balance disabled but inclination is 20 degrees" (the cathedral roof is a 4:12 pitch, around 20 degree roof slope).

I could not find any info in the WUFI help or in the Forum on just what explicit radiation balance is or how it works and what sort of impact its selection/unselection means in terms of run results.

Ideas?

Thanks - Peter
Peter Yost
BuildingGreen, Inc.
Brattleboro, VT USA
Christian Bludau
WUFI SupportTeam IBP
WUFI SupportTeam IBP
Posts: 1160
Joined: Tue Jul 04, 2006 10:08 pm -1100
Location: IBP Holzkirchen, the home of WUFI
Contact:

Re: explicit radiation balance

Post by Christian Bludau »

Hi Peter,
try to switch on the "adaptive time step control". More important then the convergence failures are usually the balances, they should be close to each other. You find them in the table appearing after the calculation.
Christian
Post Reply