WUFI 6.2 ASHRAE 160 Climate
-
Ned Lyon
- WUFI User

- Posts: 22
- Joined: Mon Jan 16, 2006 9:42 am -1100
- Location: Boston, MA - USA
- Contact:
WUFI 6.2 ASHRAE 160 Climate
WUFI 6.2 has a bug in the graph for ASHRAE 160 climate. The graph does not generate the results for conditions entered unless one toggles the AC only/AC with dehumidification. If you close and reopen the file or switch between cases, the graph data reverts to something other than the current selections for 160 interior. This appears to be only a graph update issue a the models appear to run with the selected ASHRAE 160 parameters.
Ned at SGH
-
Christian Bludau
- WUFI SupportTeam IBP

- Posts: 1263
- Joined: Tue Jul 04, 2006 10:08 pm -1100
- Location: IBP Holzkirchen, the home of WUFI
- Contact:
Re: WUFI 6.2 ASHRAE 160 Climate
Dear Ned,
thanks for the note,
we will check that.
Christian
thanks for the note,
we will check that.
Christian
-
Madonna Stewart
- WUFI User

- Posts: 6
- Joined: Mon May 06, 2019 3:36 pm -1100
- Location: Australia
Re: WUFI 6.2 ASHRAE 160 Climate
Hi Christian
For information, this is still occurring in WUFI Pro 6.3. I have to re-select the 'AC with humidification' each time I switch between different Cases. It doesn't seem to save the internal climate selection.
All the best, Madonna
For information, this is still occurring in WUFI Pro 6.3. I have to re-select the 'AC with humidification' each time I switch between different Cases. It doesn't seem to save the internal climate selection.
All the best, Madonna
-
Christian Bludau
- WUFI SupportTeam IBP

- Posts: 1263
- Joined: Tue Jul 04, 2006 10:08 pm -1100
- Location: IBP Holzkirchen, the home of WUFI
- Contact:
Re: WUFI 6.2 ASHRAE 160 Climate
Hi Madonna,
can you please check if this is solved in the latest version WUFI Pro 6.4?
You can download it using the link you got with your purchase.
Best regards,
Christian
can you please check if this is solved in the latest version WUFI Pro 6.4?
You can download it using the link you got with your purchase.
Best regards,
Christian
-
Madonna Stewart
- WUFI User

- Posts: 6
- Joined: Mon May 06, 2019 3:36 pm -1100
- Location: Australia
Re: WUFI 6.2 ASHRAE 160 Climate
Hi Christian
Yes, the above issue appears to be solved in WUFI Pro 6.4.
Thank you,
Madonna
Yes, the above issue appears to be solved in WUFI Pro 6.4.
Thank you,
Madonna