- Exterior
7/8" stucco
paperback lath
3 1/2" batt insulation
5/8" gypsum board
Interior
When this assembly was simulated, it was found that the RH stays well above 80% at the interior side of the stucco (and therefore at the exterior edge of the insulation) for extended periods of time (approaching 5-6 months).
I tried inserting a vapor barrier at various locations, adding a layer of sheathing under the paperback lath, and adding a one-inch wide ventilated air space between the paper (or sheathing, if included) and the insulation. No configuration has been able to reduce the prolonged periods of high humidity experienced at the exterior edge of the insulation.
This type of construction is fairly common in the Bay Area, and my colleagues and I are concerned that it appears as though the software is predicting that this high RH condition will always occur in this type of construction. This has lead to some difficulty in reconciling the results of the simulation with what field experience has shown to be the case.
Has anyone else had a similar experience analyzing these types of stucco assemblies?