Hi,

would you place a rain leakage in this position in case of poor workmanship or just to stress the model? Please see the image attached.
4.PNG
4.PNG (39.55 KiB) Viewed 3916 times
Capture.PNG
Capture.PNG (263.01 KiB) Viewed 3918 times
Capture.PNG
Capture.PNG (112.9 KiB) Viewed 3917 times
Regards and tanks in advance
x
Christian Bludau
WUFI SupportTeam IBP
WUFI SupportTeam IBP
Posts: 1307
Joined: Tue Jul 04, 2006 10:08 pm -1100
Location: IBP Holzkirchen, the home of WUFI
Contact:

Re: Rain leakahe in EPS wall

Post by Christian Bludau »

Hi Alberto,

If rainwater enters at this location, it will have very limited drying potential and can lead to moisture accumulation and damage within the assembly. Therefore, it is particularly important that this detail is designed and executed to be watertight.

A properly designed and correctly connected window sill should normally prevent rainwater from penetrating into this part of the construction. For that reason, I would only include a rain source here if you specifically want to assess the consequences of poor workmanship or a failure of the weatherproofing details.

Christian
Alberto Morales
WUFI User
WUFI User
Posts: 96
Joined: Tue Mar 29, 2022 10:57 pm -1100

Re: Rain leakahe in EPS wall

Post by Alberto Morales »

But, is it realistic to add that source of rain leakage in that particular position if I suspect to have poor workmanship, a failure of the weatherproofing details or being in the worse scenario?
x
Christian Bludau
WUFI SupportTeam IBP
WUFI SupportTeam IBP
Posts: 1307
Joined: Tue Jul 04, 2006 10:08 pm -1100
Location: IBP Holzkirchen, the home of WUFI
Contact:

Re: Rain leakahe in EPS wall

Post by Christian Bludau »

Yes, you can use the source there, if you want to test, what happens in the case of water can intrude there.