Hello we are building an underground concrete structure that I have been testing details in WUFI. The project can be seen here - https://www.youtube.com/watch?v=fc9kyEWZ-f8
The build up at the top of the arch or ceiling is from inside to outside - Concrete, waterproofing, 1-2 inches of foam and 24 inches of Earth.
hen I model I am seeing that the local hygrothermal load graph shows values at the point the water proofing touches the concrete so essentially there is mould growth there. But when I open the Wufi bio it is always green. It says there is no mould risk. I feel like I am doing someting incorrectly but not sure what?
I also have another situation where we are putting a radon barrier in the crawl space and then the client wants us to insulate the crawl space and bring it in the conditioned space. But when I did the WUFI analysis of that detail I also get similar readings. where wufi bio shows no risk but the local hygrothermal graph shows that the mould will be present. Am I reading it incorrectly?
Underground Concrete structure
- Screenshot 2026-06-01 174932.png (71.64 KiB) Viewed 5363 times
- Screenshot 2026-06-01 174031.png (131.86 KiB) Viewed 5363 times
- Screenshot 2026-06-01 173702.png (96.11 KiB) Viewed 5363 times
Re: Underground Concrete structure
First of all, I would recommend having a look at the WUFI guideline on typical constructions, which also explains the correct handling and interpretation of simulations (including boundary conditions and evaluation). There you can find a basement example:
https://wufi.de/en/service/downloads/#t ... structions
Regarding your first question (local hygrothermal load vs. WUFI Bio)
You are comparing two different evaluation methods:
For constructions with soil contact (like your 24 inches of earth), it is especially important to ensure:
Crawl space / conditioned space case
For your second question:
In WUFI, there is already a predefined indoor climate template for such situations:
Under User-defined indoor climates, you will find a template called “Crawlspace”.
This can be used as a starting point for modelling crawl spaces as a boundary condition.
- The local hygrothermal load graph shows temperature and relative humidity at a specific point. This can indicate conditions where mould could be possible in principle.
- WUFI Bio, on the other hand, represents a more advanced evaluation of the local hygrothermal conditions, taking into account not only temperature and relative humidity, but also the duration, dynamics and material sensitivity.
- the local RH temporarily reaches high values,
- while WUFI Bio still shows no mould risk, because the conditions are not critical long enough or not relevant in terms of growth kinetics.
- correct exterior boundary conditions (often using appropriate climate data or simplified assumptions),
- and realistic interior conditions.