IBP Air Infiltration Model

All about WUFI Pro
Post Reply
Bonilauri
WUFI User
WUFI User
Posts: 38
Joined: Mon Jul 24, 2017 8:13 am -1100
Location: Denver, CO
Contact:

IBP Air Infiltration Model

Post by Bonilauri »

Hello,
I'm using WUFI Pro 6.1 to analyze assemblies in hot, humid climates such as Florida and Queensland (Australia).

We are working with assemblies where the airtight layer is a breathable external membrane (sd = 0.5m).

The internal environment is provided with cooling and dehumidification, so the vapor flow is from the outside in.

I'm trying to set up the WUFI model to include possible condensation due to air infiltration from the outside, to condensate against the internal gypsum board. I set up the IBP Air Infiltration Model to Class C, in the internal gypsum board. However, even if I set the internal temperature at 5˚C (not the design temperature, I was just testing!), I see no condensation happening due to air leak.

Is the IBP Air Infiltration Model set up to only consider condensation through convection of internal air?

Thank you!

Enrico
Manfred Kehrer
WUFI International Support Team
WUFI International Support Team
Posts: 353
Joined: Thu Mar 10, 2005 2:17 am -1100
Location: Northbrook, IL; USA
Contact:

Re: IBP Air Infiltration Model

Post by Manfred Kehrer »

Hello Enrico,
the IBP infiltration model should be renamed to "IBP exfiltration model" as this considers only indoor moisture convection to the outside of the insulation in cold climate zones.
If you want to model vapor from the outside convecting to and condensing on the inner side of the insulation, you should probably use an air exchange rate.
Manfred
Wiss, Janney, Elstner Associates, Inc.
Official WUFI® Collaboration Partner for USA/Canada
Enjoy WUFI® :) .... It is easy and complex.
Bonilauri
WUFI User
WUFI User
Posts: 38
Joined: Mon Jul 24, 2017 8:13 am -1100
Location: Denver, CO
Contact:

Re: IBP Air Infiltration Model

Post by Bonilauri »

Hello Manfred,
Thank you for the advice!

I'm going to test it, and see what happens.

Cheers,

Enrico
Bonilauri
WUFI User
WUFI User
Posts: 38
Joined: Mon Jul 24, 2017 8:13 am -1100
Location: Denver, CO
Contact:

Re: IBP Air Infiltration Model

Post by Bonilauri »

If I wanted to simulate the equivalent infiltration of outside air of a Class A assembly (q50 = 1 m3/m2h), but using the air exchange rate, how would that translated into a 1/h value?

Thank you
Manfred Kehrer
WUFI International Support Team
WUFI International Support Team
Posts: 353
Joined: Thu Mar 10, 2005 2:17 am -1100
Location: Northbrook, IL; USA
Contact:

Re: IBP Air Infiltration Model

Post by Manfred Kehrer »

First you would need to specify what typical pressure difference to assume from outside to inside for your building enclosure. Next thing is to reduce your q50 to that pressure. Be reminded that this is typical not a linear relationship, but as you probably don't have an flow exponent, you might assume a linear relationship. Then you can calculate the ACH according to:
Bild1.jpg
Bild1.jpg (25.42 KiB) Viewed 90742 times
Manfred
Wiss, Janney, Elstner Associates, Inc.
Official WUFI® Collaboration Partner for USA/Canada
Enjoy WUFI® :) .... It is easy and complex.
Bonilauri
WUFI User
WUFI User
Posts: 38
Joined: Mon Jul 24, 2017 8:13 am -1100
Location: Denver, CO
Contact:

Re: IBP Air Infiltration Model

Post by Bonilauri »

Thank you!
Axelarris
WUFI User
WUFI User
Posts: 24
Joined: Tue Mar 25, 2014 5:44 am -1100

Re: IBP Air Infiltration Model

Post by Axelarris »

Manfred Kehrer wrote: Thu Aug 10, 2017 9:58 am -1100 First you would need to specify what typical pressure difference to assume from outside to inside for your building enclosure. Next thing is to reduce your q50 to that pressure. Be reminded that this is typical not a linear relationship, but as you probably don't have an flow exponent, you might assume a linear relationship. Then you can calculate the ACH according to:
Bild1.jpg
Since the air change source can only be applied to the entire layer, do you recommend breaking up the layer into two separate smaller layers of the same material (one has the air change source and one doesn't)? Or do you add a 5mm air space to exchange exterior air with?
Post Reply