Large increase in Water content

All about WUFI Pro
Post Reply
Alberto Morales
WUFI User
WUFI User
Posts: 87
Joined: Tue Mar 29, 2022 10:57 pm -1100

Large increase in Water content

Post by Alberto Morales »

Hi,

I have the next build-up with water repellent and foil faced PIR in both sides modelled as vapor retarder (sd=1500).

is it right?
101.PNG
101.PNG (48.01 KiB) Viewed 102 times
Evaluating the WC in the PIR I have observed irregular, non-periodic changes in the total water content what makes me think that something can be wrong in the results. any thoughts about this change in trend?
102.PNG
102.PNG (81.34 KiB) Viewed 97 times
However there are no larger differences in balances as it can also be recognized in part by the total
water content curve above
kfyukuk.PNG
kfyukuk.PNG (8.71 KiB) Viewed 96 times
Best regards and thanks in advance
x
Daniel
WUFI SupportTeam IBP
WUFI SupportTeam IBP
Posts: 154
Joined: Tue Jul 19, 2005 2:50 am -1100
Location: Fraunhofer IBP, Holzkirchen
Contact:

Re: Large increase in Water content

Post by Daniel »

Dear Alberto,

you're right, that does not look very good.

The steep vertical increases in water content are obviously not correct. However, in the total balances these problem remain unvisible - this may be because the issue is simply a slightly incorrect distribution of moisture within the building component, which is not apparent either in the total water content or in the surface moisture fluxes.

In any case, you can assume that no moisture accumulation will occur between two layers with an sd value of 1500 m. And ss the total error ist only 0,01 kg or 10 g (0,1 kg/m³ * 0,1 m³) over 10 years, the influence on the neighbour materials remains completely negligable.

In other words, to sum up: You can perform a normal evaluation.

best regards
Daniel
Dr.-Ing. Daniel Zirkelbach, Deputy Head of Department Hygrothermics, IBP Holzkirchen
Alberto Morales
WUFI User
WUFI User
Posts: 87
Joined: Tue Mar 29, 2022 10:57 pm -1100

Re: Large increase in Water content

Post by Alberto Morales »

thanks Daniel once again.

two more question:

1- Could the "Assessing the Risk of Interstitial Condensation Runoff" guideline be applied for a foil face PIR insulation which is between an unventilated cavity and concrete?

2- could be used these formulas:

µ* = 0.09 · Rmet / (3.5 · Dx*) = 0.026 · Rmet / Dx*
lambda* = Dx* / Rnon-met

for the case we have unventilated air layer facing in one side with a brick and the other side with a face foil aluminum PIR insulation, which value should we take? the one from the column Rmet to calculate µ* and lambda*?