Large increase in Water content

All about WUFI Pro
Post Reply
Alberto Morales
WUFI User
WUFI User
Posts: 89
Joined: Tue Mar 29, 2022 10:57 pm -1100

Large increase in Water content

Post by Alberto Morales »

Hi,

I have the next build-up with water repellent and foil faced PIR in both sides modelled as vapor retarder (sd=1500).

is it right?
101.PNG
101.PNG (48.01 KiB) Viewed 247 times
Evaluating the WC in the PIR I have observed irregular, non-periodic changes in the total water content what makes me think that something can be wrong in the results. any thoughts about this change in trend?
102.PNG
102.PNG (81.34 KiB) Viewed 242 times
However there are no larger differences in balances as it can also be recognized in part by the total
water content curve above
kfyukuk.PNG
kfyukuk.PNG (8.71 KiB) Viewed 241 times
Best regards and thanks in advance
x
Daniel
WUFI SupportTeam IBP
WUFI SupportTeam IBP
Posts: 156
Joined: Tue Jul 19, 2005 2:50 am -1100
Location: Fraunhofer IBP, Holzkirchen
Contact:

Re: Large increase in Water content

Post by Daniel »

Dear Alberto,

you're right, that does not look very good.

The steep vertical increases in water content are obviously not correct. However, in the total balances these problem remain unvisible - this may be because the issue is simply a slightly incorrect distribution of moisture within the building component, which is not apparent either in the total water content or in the surface moisture fluxes.

In any case, you can assume that no moisture accumulation will occur between two layers with an sd value of 1500 m. And ss the total error ist only 0,01 kg or 10 g (0,1 kg/m³ * 0,1 m³) over 10 years, the influence on the neighbour materials remains completely negligable.

In other words, to sum up: You can perform a normal evaluation.

best regards
Daniel
Dr.-Ing. Daniel Zirkelbach, Deputy Head of Department Hygrothermics, IBP Holzkirchen
Alberto Morales
WUFI User
WUFI User
Posts: 89
Joined: Tue Mar 29, 2022 10:57 pm -1100

Re: Large increase in Water content

Post by Alberto Morales »

thanks Daniel once again.

two more question:

1- Could the "Assessing the Risk of Interstitial Condensation Runoff" guideline be applied for a foil face PIR insulation which is between an unventilated cavity and concrete?

2- could be used these formulas:

µ* = 0.09 · Rmet / (3.5 · Dx*) = 0.026 · Rmet / Dx*
lambda* = Dx* / Rnon-met

for the case we have unventilated air layer facing in one side with a brick and the other side with a face foil aluminum PIR insulation, which value should we take? the one from the column Rmet to calculate µ* and lambda*?
x
Christian Bludau
WUFI SupportTeam IBP
WUFI SupportTeam IBP
Posts: 1302
Joined: Tue Jul 04, 2006 10:08 pm -1100
Location: IBP Holzkirchen, the home of WUFI
Contact:

Re: Large increase in Water content

Post by Christian Bludau »

Hi Alberto,
regarding your questions:
1) yes, the condensation in air layers part
2) yes, the Rmet values - these should always be used if there is at least one metallic surface connected to the air gap
Christian
Alberto Morales
WUFI User
WUFI User
Posts: 89
Joined: Tue Mar 29, 2022 10:57 pm -1100

Re: Large increase in Water content

Post by Alberto Morales »

thanks, but how can we evaluate the risk of interstitial condensation in a wall which includes face aluminum foil PIR as none of the guidelines include steps to follow for cases with this type of close-cell insulation?.
aaaa.PNG
aaaa.PNG (70.06 KiB) Viewed 63 times
as the difference in water content over 10 years is around 25g (above ± 10 - 20 g/year) in the PIR, I have some concerns.

Any thoughts?
x
Daniel
WUFI SupportTeam IBP
WUFI SupportTeam IBP
Posts: 156
Joined: Tue Jul 19, 2005 2:50 am -1100
Location: Fraunhofer IBP, Holzkirchen
Contact:

Re: Large increase in Water content

Post by Daniel »

In close-cell insulation no runoff can occur. The water remains in the cells where it forms.

If necessary, an increase in thermal conductivity should be taken into account—as a general guideline, one can assume that for water contents up to 2% by volume or 20 kg/m³, the effect of moisture is already factored into the declared lambda values—only higher values need to be evaluated.
Dr.-Ing. Daniel Zirkelbach, Deputy Head of Department Hygrothermics, IBP Holzkirchen
Alberto Morales
WUFI User
WUFI User
Posts: 89
Joined: Tue Mar 29, 2022 10:57 pm -1100

Re: Large increase in Water content

Post by Alberto Morales »

How is it possible to state that “In closed-cell insulation, no runoff can occur. The water remains in the cells where it forms”?

Correct me if I am wrong, what I undersand is that PIR is a highly moisture-resistant, closed-cell foam, so water cannot easily penetrate or accumulate within its sealed cells. Unlike wood fibre, it does not readily absorb or wick water through the material. If exposed to rain, leaks, or internal vapour, water should mainly remain on the external surface (there are also aluminium foil facings on both sides of the PIR board acting as vapor barrier) and run off, rather than enter the closed cells. Therefore, I do not understand how water could “remain in the cells where it forms.”
1.PNG
1.PNG (152.55 KiB) Viewed 8 times
Water content at outer 1cm of PIR.png
Water content at outer 1cm of PIR.png (20.18 KiB) Viewed 8 times
RH at outer 1cm of PIR.png
RH at outer 1cm of PIR.png (25.73 KiB) Viewed 8 times
Last edited by Alberto Morales on Thu Sep 17, 2026 11:20 pm -1100, edited 2 times in total.
x
Daniel
WUFI SupportTeam IBP
WUFI SupportTeam IBP
Posts: 156
Joined: Tue Jul 19, 2005 2:50 am -1100
Location: Fraunhofer IBP, Holzkirchen
Contact:

Re: Large increase in Water content

Post by Daniel »

I fear you have to explain and to hope that one can understand! Even from most open cell foams only little amounts will drain!
Dr.-Ing. Daniel Zirkelbach, Deputy Head of Department Hygrothermics, IBP Holzkirchen