Large increase in Water content
Post by Alberto Morales »
I have the next build-up with water repellent and foil faced PIR in both sides modelled as vapor retarder (sd=1500).
is it right?
Evaluating the WC in the PIR I have observed irregular, non-periodic changes in the total water content what makes me think that something can be wrong in the results. any thoughts about this change in trend?
However there are no larger differences in balances as it can also be recognized in part by the total
water content curve above
Best regards and thanks in advance
Re: Large increase in Water content
Post by Daniel »
Dear Alberto,
you're right, that does not look very good.
The steep vertical increases in water content are obviously not correct. However, in the total balances these problem remain unvisible - this may be because the issue is simply a slightly incorrect distribution of moisture within the building component, which is not apparent either in the total water content or in the surface moisture fluxes.
In any case, you can assume that no moisture accumulation will occur between two layers with an sd value of 1500 m. And ss the total error ist only 0,01 kg or 10 g (0,1 kg/m³ * 0,1 m³) over 10 years, the influence on the neighbour materials remains completely negligable.
In other words, to sum up: You can perform a normal evaluation.
best regards
thanks Daniel once again.
two more question:
1- Could the "Assessing the Risk of Interstitial Condensation Runoff" guideline be applied for a foil face PIR insulation which is between an unventilated cavity and concrete?
2- could be used these formulas:
µ* = 0.09 · Rmet / (3.5 · Dx*) = 0.026 · Rmet / Dx*
lambda* = Dx* / Rnon-met
for the case we have unventilated air layer facing in one side with a brick and the other side with a face foil aluminum PIR insulation, which value should we take? the one from the column Rmet to calculate µ* and lambda*?
regarding your questions:
1) yes, the condensation in air layers part
2) yes, the Rmet values - these should always be used if there is at least one metallic surface connected to the air gap
thanks, but how can we evaluate the risk of interstitial condensation in a wall which includes face aluminum foil PIR as none of the guidelines include steps to follow for cases with this type of close-cell insulation?.
as the difference in water content over 10 years is around 25g (above ± 10 - 20 g/year) in the PIR, I have some concerns.
Any thoughts?
Post by Daniel »
In close-cell insulation no runoff can occur. The water remains in the cells where it forms.
If necessary, an increase in thermal conductivity should be taken into account—as a general guideline, one can assume that for water contents up to 2% by volume or 20 kg/m³, the effect of moisture is already factored into the declared lambda values—only higher values need to be evaluated.
How is it possible to state that “In closed-cell insulation, no runoff can occur. The water remains in the cells where it forms”?
Correct me if I am wrong, what I undersand is that PIR is a highly moisture-resistant, closed-cell foam, so water cannot easily penetrate or accumulate within its sealed cells. Unlike wood fibre, it does not readily absorb or wick water through the material. If exposed to rain, leaks, or internal vapour, water should mainly remain on the external surface (there are also aluminium foil facings on both sides of the PIR board acting as vapor barrier) and run off, rather than enter the closed cells. Therefore, I do not understand how water could “remain in the cells where it forms.”
Water content at outer 1cm of PIR.png (20.18 KiB) Viewed 44584 times
RH at outer 1cm of PIR.png (25.73 KiB) Viewed 44584 times
Last edited by Alberto Morales on Thu Sep 17, 2026 11:20 pm -1100, edited 2 times in total.
Post by Daniel »
We speak about dew water which condenses inside the insulation foam - your question was about interstital condensation. This cannot runoff.
Other moisture cannot enter the insualation but at most condense on the surfaces.
I was talking about that water that forms between surfaces...mainly between vapor retarder and PIR as the RH is above 95% (see image RH outer 1cmm of PIR) but wáter content keeps stable...any thoughts?
How can you detect based on WUFI result when condensation/run off will occur between surfaces and when condensation will occur inside the close cell ínsula (PIR) pores?
In the image above, the difference in water content in PIR over 10 years is around 25g (above ± 10 - 20 g/year) in the PIR, is It a concern? You mentioned above that that ± 10 - 20 g/year is not...
In WUFI, liquid water cannot accumulate directly between two adjacent material layers because the model does not represent an interface cavity. If you want to evaluate interstitial condensation and possible runoff at an interface, you would need to introduce an explicit air layer in the model. Otherwise, any moisture is always assigned to the neighbouring material cells. In your case, the reported moisture is therefore stored within the PIR layer rather than as free water between surfaces.
As for the moisture increase of about 25 g over 10 years, I would not consider this a concern. PIR is generally not moisture-sensitive, and such a small absolute change is unlikely to have any significant effect on its durability or thermal performance. The ±10-20 g/year criterion is typically used as an indicator of long-term moisture accumulation trends rather than as a material damage threshold.
Thanks for the reply.
in my case, do I need to evaluate the run off in the 1mm air layer which is facing with the foil of the insulation, or between PIR and Foil?
which in the "Example 1: Exterior wall " of the guideline, this explicit air layer was not created between insulation and vapor retarder?
The moisture shown in your results is located within the PIR, which is enclosed by vapour-tight aluminium facings on both sides. In a one-dimensional calculation, practically no additional moisture can enter this layer. The variations therefore mainly represent a redistribution of the initial moisture within the PIR caused by the changing temperature gradient.
You can either disregard this redistribution as unproblematic or check whether the assumed initial moisture content is too high, since PIR is likely to be installed with a considerably lower initial moisture content than that corresponding to 80% RH.
Any runoff assessment would refer to the air layer adjacent to the outer aluminium facing, not to the interface between the PIR core and its factory-applied facing. Under typical climatic boundary conditions, no problematic condensation is expected on the outer side of the facing in this configuration.